structural-eng
Structural
- Jan 26, 2017
- 39
If Lpile is supposed to use working loads, which makes sense to me because foundation movement usually governs the design, should the NESC 250B case be considered without the overload factors? It seems like 250B is an ultimate load case given the OLF and I've seen published documents that refer to it as an ultimate stress design. I have a dead end structure where the ultimate 250B load is higher than the ulitmate ASCE (sim 250C) load but if I look at unfactored loads the ASCE is higher than the NESC 250B case. Everything is likely to be controlled by deflection including the steel framing for the dead end so I really have 2 questions. Which load should be considered for the foundation design using Lpile if pier movement is going to govern and should the steel deflections be checked using the working load for both the NESC 250B and the ASCE or should the deflection be calculated using NESC ultimate loads and ASCE working loads?