I have a customer that has a substation that they want the gravel replaced. Is there a IEEE Std for this work? If so ehat is it?
 
Replies continue below

Recommended for you

IEEE Std 80 deal with surfacing material resistivity to maintain the allowable step and touch potential at desirable level as a function of the resistivity and thickness of a crushed stone layer .

From the civil engineering standpoint, crushed rock may be use as soil stabilizer, internal roadway, sub drainage, etc.

Crushed stone # 2 without fines material is expected to have a wet resistivity around 2000 to 3000 Ohm-meter. A layer of 4 inches inside the substation and 3 ft beyond the fence usually provide may have good results.
 