Substation Short Circuit

Status
Not open for further replies.

Mbrooke

Electrical
Nov 12, 2012
2,546
What would cause this? How would high voltage get into the control house? I'm guessing CT or VT short circuited internally?




I have a fear of relay circuits now lol.
 
Replies continue below

Recommended for you

A protection planner I knew had a piece of black glass on his desk. I think it used to be switchyard gravel, a 230kv CT had failed. In the control room the covers were blown off the relays. I take it some of the fault voltage or localized ground rise came in through the control cables. At college our professor had a couple guys check out 600v wire with a 15kv Hi-Pot set. The corona glowed but the insulation did not puncture right away. The jacket on the control cables would more than double the available insulation.

Bill
 
Could be ground potential rise as well with a poor earthing grid. I see smoke rising from the ground near the control hut.
 