structural-eng
Structural
- Jan 26, 2017
- 39
I have a couple questions about designing base plates for substation structures. Can the base plate design method shown in ASCE 113 be used if column is an HSS and the base plate is open within the column for venting and drainage? I typically detailed 4" diameter holes for venting and drainage when using HSS8x8 column which meets the galvanizing associations minimum opening requirements but the fabricators constantly want larger openings. I know that the larger openings help improve drainage and require less tipping of the members but they also cut down the structural capacity of the base plate. I typically like to ensure that the base plates work by plate bending or a combination of torsion and plate bending and the large slots that the fabricators like to use don't allow me to look at the base plate bending the way I would like to.
I have seen other threads on here that talk about detailing the column to extend into the base plate and then fillet welding the base plate to the column on the top and bottom. It seems that doing this creates a "flange plate" more so than a base plate and that you would need to be able to develop fixity in the welded connection between the plate and the HSS column with this condition but maybe I'm missing something.
We have detailed the weld between the column and the base plate as a full penetration weld in the past and are getting requests to find a way to make a single pass fillet weld work instead because of the large about of labor required for full penetration welds. I've seen some other threads on here where there was talk about full penetration welds but it wasn't clear if that was only for transmission structures (per ASCE 48-11) or if there are others that are using them for substations as well.
I have seen other threads on here that talk about detailing the column to extend into the base plate and then fillet welding the base plate to the column on the top and bottom. It seems that doing this creates a "flange plate" more so than a base plate and that you would need to be able to develop fixity in the welded connection between the plate and the HSS column with this condition but maybe I'm missing something.
We have detailed the weld between the column and the base plate as a full penetration weld in the past and are getting requests to find a way to make a single pass fillet weld work instead because of the large about of labor required for full penetration welds. I've seen some other threads on here where there was talk about full penetration welds but it wasn't clear if that was only for transmission structures (per ASCE 48-11) or if there are others that are using them for substations as well.