Specifications for a single story warehouse foundation call for a PIP wall foundation (no change in footing) to a depth of 4' with #4 rebar lengthwise at 3' OC. The contractor has offered a reduced cost if concrete masonry unit (same thickness) is used. This appears to be OK for this application (building permit approved, I have authority to change). Should rebar be still be installed in CMU joint same as PIP or is no rebar OK? Lots of existing area foundations are without the rebar, but due to 40' span and 4" slab, the PIP was preferred.
 
Replies continue below

Recommended for you

The reinforcement requirements depends upon the combination of height of wall and the combined axial and wind loads (plus seismic where req'd).
A good rule of thumb for prelim is #5 bars at 48" vert and horiz.
 
CMU is an easy substitute, but review the circumstances with a local engineer. Minimal detailing recommendations should be observed. Many times, the steel is present only to control non-structural cracking. Your warehouse application sounds non-architecturally significant - meaning only that the likelihood of a lawsuit for non-structural cracks is not significant. The code allows unreinforced foundations, and they perform well within limits. Even these however should have control joints to control cracking. CMU with horizontal joint reinforcement performs well for minimal loading.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top