Subtransient Reactance of Generator

Status
Not open for further replies.

HamidEle

Electrical
Feb 20, 2007
309
Who know the subtransient reactance data of 35MW generators? Thanks in advance.
 
Replies continue below

Recommended for you

Hydro unit, gas turbine, or steam? rpm or # of poles? Hz? Manufacturer?

Typical values 0.12 - 0.25 for 2-pole machines.
 
It is a Hydro typo. 50HZ
poles? Manufacturer? I don't know.

We are working on an international project based on Guesses, which is driving me nuts.
 
I think that is something you are going to have to get from the manufacturer. Do you have any hints or clues to who that might be?

rmw
 
On a 50Hz 4 pole generator 1500rpm (diesel)400/231vac up to 2.5mW we use 0.8.
 
There is a table of typical values in Chapter 5 of the Areva PRAG. ftp://ftp.areva-td.com/NPAG/Chap5-46-77.pdf
Regards
Marmite
 
Who know the subtransient reactance data of 0.556MVA generators? and where can ? find these values of generators from? thanks
 
Sub-transient, Transient & steaDY STATE reactance of machines are dependent on macine size.

Medium size machine:-

Subtransient Reactance = 0.16 to 0.24
Transient Reactance = 0.2 to 0.28
Synhronous reactance = 2.25 to 3.0

Synchronous reacance value is inversly proportional to short circuit ratio of machine. For example SC Raio = 0.4 then Xs = 1/0.4 = 2.5

Thanks
 