Suction line piping 1

Status
Not open for further replies.

AirHandlerReefer

Materials
Mar 8, 2012
1
Current installation of a low temperature refrigeration box. The boss made me redo the suction line piping. He says that because the Evaporator is above the compressor in this application the suction line should be looped to the highest point of the coil before dropping to the compressor. He told me to figure out my mistake. It cant be an oil return issue...can it?
 
Replies continue below

Recommended for you

You do not want any liquid refrigerant leaving the evaporator, only vaporized refrigerant.
 
And this is related to Electrical Engineering how? You might want to repost this in the ME section.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> faq731-376
 
... but you do want the vapor to carry oil back to the compressor, so you put a trap between the evaporator and the bottom of that 'riser'.

Search on 'refrigerant piping' to find handbooks with hints about subtle, er, traps, you might encounter.



Mike Halloran
Pembroke Pines, FL, USA
 