charz
Electrical
- Jan 11, 2011
- 95
In a 3 phase, particular motor feeder, the Power factor suddenly reduced from 0.98 to 0.82. The circuit is shown below,
The company is not sending me to the plant, anyway I would like to know the cause of the trouble for my experience. I'm thinking of blowing of capacitor fuse in one phases. If so, what would be the Kvar output from the capacitor bank from the 2 capacitor banks.It means the two capacitor banks are in series with applied voltage of 6kV. Also the operator observed the noise from the 6% series reactor. What could have possibly went wrong?
The company is not sending me to the plant, anyway I would like to know the cause of the trouble for my experience. I'm thinking of blowing of capacitor fuse in one phases. If so, what would be the Kvar output from the capacitor bank from the 2 capacitor banks.It means the two capacitor banks are in series with applied voltage of 6kV. Also the operator observed the noise from the 6% series reactor. What could have possibly went wrong?