I have a new application. It is essentially a copy of another installation in the same geographic area.
In the original installation some assumptions were made with regards to heat load from electrical gear. The actual chiller loads we have been seeing are about 70% of what we thought design was based on trend data.
My issue is: In the new installation, I want to size the new chillers closer to the load. I am going to have one absorption unit and one centrifugal unit with a VFD.
The load break down is (in percentage of operating time)
200-300 tons - 54%
300-324 tons - 46%
325-349 tons - 25%
350-374 tons - 13%
375-399 tons - 6%
400-424 tons - 3%
425-449 tons - 1%
450-474 tons - 1%
475-499 tons - <1%
Over 500 tons - <1% (Peak tonnage was 765)
The original system was two 500 ton chillers. My thoughts are - sizing the absorption unit at 350 tons and operating it as the primary chiller. This size is due to problems with absorption unit turn down, I think it should be running as close to full load as possible.
My gut tells me that with a VFD, I can size the centrifugal as big as I want to cover my butt for back up operation. But my experience with chilled water systems says - "Don't be too hasty Grasshopper".
Do I size them both at the same tonnage? Suggestions?
In this new engineering world we live in (i.e. me being relatively inexperienced with no knowledgeable mentor where I work - just non-detailed manager types) this forum is awesome for checking out ideas.
In the original installation some assumptions were made with regards to heat load from electrical gear. The actual chiller loads we have been seeing are about 70% of what we thought design was based on trend data.
My issue is: In the new installation, I want to size the new chillers closer to the load. I am going to have one absorption unit and one centrifugal unit with a VFD.
The load break down is (in percentage of operating time)
200-300 tons - 54%
300-324 tons - 46%
325-349 tons - 25%
350-374 tons - 13%
375-399 tons - 6%
400-424 tons - 3%
425-449 tons - 1%
450-474 tons - 1%
475-499 tons - <1%
Over 500 tons - <1% (Peak tonnage was 765)
The original system was two 500 ton chillers. My thoughts are - sizing the absorption unit at 350 tons and operating it as the primary chiller. This size is due to problems with absorption unit turn down, I think it should be running as close to full load as possible.
My gut tells me that with a VFD, I can size the centrifugal as big as I want to cover my butt for back up operation. But my experience with chilled water systems says - "Don't be too hasty Grasshopper".
Do I size them both at the same tonnage? Suggestions?
In this new engineering world we live in (i.e. me being relatively inexperienced with no knowledgeable mentor where I work - just non-detailed manager types) this forum is awesome for checking out ideas.