Gaply
Chemical
- Jun 9, 2009
- 4
We have a 98% sulfuric acid tank of mid 1980's construction on site that was recently inspected. The tank is a vertical tank with a cone roof of about 40m3 capacity. The roof has a 1" vent pipe that goes through a dessicant trap. The tank also has a 3" overflow pipe off the tank wall. The overflow connection has a goose-neck trap at the bottom that was filled with an inert liquid (I think this was a silicon oil) to ensure normal venting goes through the vent line rather than the overfill line. When the gooseneck in the overfill line was inspected it was found liquid in had reacted with the acid vapour and set solid. Obviously this would have resulted in a very dangerous situation if the tank had ever been overfilled in error, possibly causing catastrophic failue. As a result no liquid has been put into the gooseneck yet. Apart form raising this issue my question is does anyone know what is a safe inert liquid that can be used in the gooseneck in future?