Knowing that the sum of the current is 0 during the fault, can we say if the sum of the magnetic forces is also 0 during a short circuit?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Fab = -Fba. Same is true for all forces between conductors, therefore ∑F=0. There is no net force on the bundle of conductors, omly between conductors.cuky2000 said:∑F= Fab+ Fac+Fba+Fbc+Fca+Fcb =0
I will accept that.There is no net force on the bundle of conductors, omly between conductors.
There are definitely forces on the individual phase conductors.On your drawing of flat parallel busbars, there is no force on the 3-phase support caused by fault currents.
I was referencing the top drawing, assuming the 4 vertical gray columns were the legs of the three-phase support.waross said:Note that the three phase support {Cross Arm} is not shown in the drawing. Only the single phase supports are shown.
Yes. I agree.I was referencing the top drawing, assuming the 4 vertical gray columns were the legs of the three-phase support.