Sump pit of lift core reinforcement

LewisLiew

Civil/Environmental
Apr 14, 2015
19
Image1 below shown reinforcement for sump pit. Would like to know why reinforcement in Image2 not suitable.

Screenshot_20250103-223407_ACC.jpg
IMG-20250103-WA0111.jpg
 
Replies continue below

Recommended for you

The attached picture seems to be scaled and apparently the height of raft 1500 mm . The top reinf. mesh spacing 100 mm is not suitable for concrete placement .
Instead of reinf. mesh basket ( image 2 ), you may add a quantity of extra reinforcement at least equal to that interrupted by the sump pit added
on the sides of the opening which is common practice.
 