Very cool (literally), thanks for the post.
 
Thanks for the link.

Great feat of engineering.
 
My firm performed the final acceptance test on that cable.
A very interesting project indeed.
Thanks for the link.
 
dpmac

Any chance you can share what sort tests were conducted ?
 
Please do, i was wondering the same thing. What tests? Did they put continous PD monitors on this cable? What a shame if they didnt.
 
Sorry I don't have more information, we only performed an after installation withstand test for the installer. Test voltage was 114kVAC for one hour. I am sure there were a number of other tests performed by others pertaining to both cooling equipment, cable and cable terminations.

There was a 34kV HTS installation in Albany NY a couple of years ago. We supplied an AC supply and HV Bridge so others could perform periodic PF tests as the cable was brought to final temp over a long period of time. I believe a DC test was performed prior to installation on that project.

 
Thanks dpmac.

This is indeed an amazing development by US engineers. Kudos to them.
 
DC hipot?? Really??
 
Thanks for the link.
New generation!!!! Next step: transformer and generator?
 
ZogZog:

We did perform PD testing during the 60Hz AC acceptance test on the 138kV circuit.

Regarding the DC acceptance test on the 34kV circuit, they may have had other concerns besides PD on a cable of this type. The insulation is not extruded and is operating at 65 Kelvin. I assume the possibility of space charges left over from DC testing was not a priority. I believe the mechanical stresses involved with the extreme low temperatures may be a bigger concern.

I will say the plumbing work involved with the cooling on both projects was very impressive!
 
I'm surprised at the "fault" aspect I'm reading here.

Used to be if a super superconducting cable got over amped -> the B-field got too large -> the cable went non-SC exploding at the first spot that went non-SC.

Now they're saying that it's a feature that limits damage and doesn't hurt the cable.

Keith Cress
kcress -
 
dpmac,

Sounds good, I missed the 34kV part.
 