I have a 13.8-4.16kV transformer (D-Y). The neutral is impedance grounded (400A @ 10 seconds). The transformer feeds a lineup of switchgear. According to 250.30(A)(1), Exception 2 of the NEC, is worded such that a wire type bonding jumper from the transformer enclosure to the "Incomming Main" of the 4.16kV switchgear wouldn't be required.
Because I have an impedance grounded transformer, I don't know that 250.30(A)(2) applies at all.
Backing away from the code, the goal here is to provide a path back to the source for ground fault current. The path should be able to carry the current long enough for the relaying to actuate. Since the ground current is limited to 400A, I would think that the 5kV shields on the lowside feeder cables should suffice? Do I really need to run a wire type supply side bonding jumper with the 4160 circuit conductors from the outdoor transformer to the switchgear building?
In addition to this. We have a ground loop around the outdoor transformer that will be tied to the ground loop outside the switchgear building. I'm thinking that this makes this system NOT separately derived.
Because I have an impedance grounded transformer, I don't know that 250.30(A)(2) applies at all.
Backing away from the code, the goal here is to provide a path back to the source for ground fault current. The path should be able to carry the current long enough for the relaying to actuate. Since the ground current is limited to 400A, I would think that the 5kV shields on the lowside feeder cables should suffice? Do I really need to run a wire type supply side bonding jumper with the 4160 circuit conductors from the outdoor transformer to the switchgear building?
In addition to this. We have a ground loop around the outdoor transformer that will be tied to the ground loop outside the switchgear building. I'm thinking that this makes this system NOT separately derived.