jwilson3
Electrical
- Dec 20, 2001
- 45
The 2002 NEC "Handbook" provides an example of how to size a transformer and select overcurrent device ratings for a 4160v supply to a 480v 100hp fire pump and 1.5hp jockey pump. It's covered in NEC695.5(A)&(B) and is a straight forward process to select a 150kva transformer.
Where two 4160v sources are needed (normal & backup) 695.5(C) is used. The transformer size is selected per 695.5(C)(1) in the same manner as above. The OC devices are sized per 695.5(C)(2), also as above, to carry the locked rotor of both pumps.[100a on pri. and 850a on sec.]
NEC 695.5(C)(2) has the further requirement that the transformer size be "coordinated" so that the OC devices provide proper protection per 450.3 and Table 450.3(A)
The 150kva size is now inadequate since the 100a pri device is 481% of rating and the sec. device is 470%, therefore a 300kva transformer must be used.
Why is the transformer rating required to be greater when served from two sources than when served from one?
Where two 4160v sources are needed (normal & backup) 695.5(C) is used. The transformer size is selected per 695.5(C)(1) in the same manner as above. The OC devices are sized per 695.5(C)(2), also as above, to carry the locked rotor of both pumps.[100a on pri. and 850a on sec.]
NEC 695.5(C)(2) has the further requirement that the transformer size be "coordinated" so that the OC devices provide proper protection per 450.3 and Table 450.3(A)
The 150kva size is now inadequate since the 100a pri device is 481% of rating and the sec. device is 470%, therefore a 300kva transformer must be used.
Why is the transformer rating required to be greater when served from two sources than when served from one?