I have recently looked at a number of installations involving VFDs on a stand alone transformer where I believe that there may be a resonance issue.
The transformers are rural, commonly fed by 10 + KW of overhead 11KV or 22KV lines and are feeding a VFD. Usually, there is no other load.
The VFDs have been installed in a manner to minimize the common mode leakage currents and voltages.
The VFDs are fed via a broadband passive filter.
Transformers are generally in the 100KVA - 500KVA sizing.
Supply is MEN.
On the supply side of the VFD, there is a ripple voltage appearing which is synchronized to the switching frequency of the drive. When the drive is stopped, the ripple disappears.
Altering the configuration in a manner that has a major impact on the common mode leakage, has no impact on the ripple voltage.
Adding capacitance (say 10KVAR) on the output of the transformer significantly increases the ripple voltage.
I recently came across one installation with an active front end drive where the ripple voltage phase to neutral (230V P-N 50Hz) was 128Vpk-pk and this burnt out two electricity meters and a PQ meter after a very short time.
In most cases, there is a length of underground cable on either the input or the output of the transformer.
It looks like the transformer is resonating with the cable capacitance and being stimulated by the common mode impulses from the drive. The magnitude of the resonance appears to be load limited rather than common mode amplitude related.
Can anybody suggest a practical solution to this? I know of one installation where they changed the transformer for a different brand and the problem was cured.
Best regards,
Mark
Mark Empson
Advanced Motor Control Ltd
The transformers are rural, commonly fed by 10 + KW of overhead 11KV or 22KV lines and are feeding a VFD. Usually, there is no other load.
The VFDs have been installed in a manner to minimize the common mode leakage currents and voltages.
The VFDs are fed via a broadband passive filter.
Transformers are generally in the 100KVA - 500KVA sizing.
Supply is MEN.
On the supply side of the VFD, there is a ripple voltage appearing which is synchronized to the switching frequency of the drive. When the drive is stopped, the ripple disappears.
Altering the configuration in a manner that has a major impact on the common mode leakage, has no impact on the ripple voltage.
Adding capacitance (say 10KVAR) on the output of the transformer significantly increases the ripple voltage.
I recently came across one installation with an active front end drive where the ripple voltage phase to neutral (230V P-N 50Hz) was 128Vpk-pk and this burnt out two electricity meters and a PQ meter after a very short time.
In most cases, there is a length of underground cable on either the input or the output of the transformer.
It looks like the transformer is resonating with the cable capacitance and being stimulated by the common mode impulses from the drive. The magnitude of the resonance appears to be load limited rather than common mode amplitude related.
Can anybody suggest a practical solution to this? I know of one installation where they changed the transformer for a different brand and the problem was cured.
Best regards,
Mark
Mark Empson