I'm trying to fill out a table for 3 phase ac induction motors.
A 50HP motor has ratings of 148 full load amps and 808 locked rotor current at 200 volts.
If power supply is 208 volts, I use a proportional equation which results in a higher locked rotor current (about 840)due to increased voltage. Also, for full load amps i use the equation:
current = (HP*746)/(1.73*Appliedvoltage*Efficiency*powerfactor)
This says full load amps will drop (to about 142A) due to an increased voltage.
However, I have read that applying increased voltage above ratings can result in saturation of the magnetizing part which would result in an increase of drawn current, not a decrease as is stated in the equation. Is it because this saturation occurs when supplied voltage is well above the rated voltage?
Thanks!
I'm trying to fill out a table for 3 phase ac induction motors.
A 50HP motor has ratings of 148 full load amps and 808 locked rotor current at 200 volts.
If power supply is 208 volts, I use a proportional equation which results in a higher locked rotor current (about 840)due to increased voltage. Also, for full load amps i use the equation:
current = (HP*746)/(1.73*Appliedvoltage*Efficiency*powerfactor)
This says full load amps will drop (to about 142A) due to an increased voltage.
However, I have read that applying increased voltage above ratings can result in saturation of the magnetizing part which would result in an increase of drawn current, not a decrease as is stated in the equation. Is it because this saturation occurs when supplied voltage is well above the rated voltage?