tinfoil
Electrical
- Jun 24, 2004
- 351
I am in the process of replacing and upgrading the supply transformer for a small utility of 3000 customers.
The source is 44kV delta, and the existing transformer steps down the voltage via a delta-delta connection to supply a three-wire medium voltage (26.4kV) subtransmission system.
My dilemma is that 26.4kV delta is a VERY rare voltage in my general area, which is domininated by 16/27.6kV Wye systems. I would like to evaluate the conversion of my system to 27.6kV wye, by specing the appropriate transformer and reconstructing my 44-27.6kV substation as appropriate.
Much of the 26.4 delta system already has underbuilt 2400/4160V four-wire distribution present (complete with a neutral), and there is sufficient clearance on the rest to accommodate the addition of a neutral.
Obviously, all of my 26400:4160 stations are presently connected delta-wye, as are several industrial customers. There are several small hydroelectric facilities connected to the delta subtransmission system as well. Each such transformer has off-load tapchangers which could make the adjustment from 26.4 line-to-line to 27.6kV line-to-line.
Does anyone forsee any issues with continuing to connect each customer and substation transformer as a three-wire primary (now 27.6kV) and supplying as before?
Any problems with connecting the low-side neutral of any of these existing delta-wye transformers with a 4-wire secondary to the new 27.6kV neutral?
The source is 44kV delta, and the existing transformer steps down the voltage via a delta-delta connection to supply a three-wire medium voltage (26.4kV) subtransmission system.
My dilemma is that 26.4kV delta is a VERY rare voltage in my general area, which is domininated by 16/27.6kV Wye systems. I would like to evaluate the conversion of my system to 27.6kV wye, by specing the appropriate transformer and reconstructing my 44-27.6kV substation as appropriate.
Much of the 26.4 delta system already has underbuilt 2400/4160V four-wire distribution present (complete with a neutral), and there is sufficient clearance on the rest to accommodate the addition of a neutral.
Obviously, all of my 26400:4160 stations are presently connected delta-wye, as are several industrial customers. There are several small hydroelectric facilities connected to the delta subtransmission system as well. Each such transformer has off-load tapchangers which could make the adjustment from 26.4 line-to-line to 27.6kV line-to-line.
Does anyone forsee any issues with continuing to connect each customer and substation transformer as a three-wire primary (now 27.6kV) and supplying as before?
Any problems with connecting the low-side neutral of any of these existing delta-wye transformers with a 4-wire secondary to the new 27.6kV neutral?