I'm going in circles here.
This is what the maker describes but how does this distill into hardware?
The drive draws 48A. Wire size 125% x 48A = 60A
That's a 30,60,100 disconnect.
But then they state a 75A breaker. I'd expect the breaker would be in the main panel. But, It's going to need wire for 75A x 125% after it?
Then they state a 100A fuse which is one of those ultra-high-speed fuses to protect the drive from rapid disassembly issues.
How I'm taking it that this is: a 75A breaker feeding 75 x 125A (75°C) wire to the control panel.
At the control enclosure a 100A sized Disconnect loaded with 100A Ultra Fast Fuses.
Seems wrong that a 48A load is demanding 100A hardware and 75A++ wiring.