Surge arrester on the earthed neutral point of HV transformer

essamalbanna

Electrical
Mar 31, 2013
3
I'm searching for a logical explanation or practical purpose for installing a lightning arrester at both neutral points of the transformer 220/66 KV, YNynd11, Although both neutral points are connected directly to earth through a disconnector!.
View attachment 2014
 

Attachments

  • Untitled_tz6l5v.jpg
    Untitled_tz6l5v.jpg
    15.7 KB · Views: 3
Last edited:
That provides some protection when the disconnector is opened.
 