Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Surge Arrester Rating for Delta Tertiary

Status
Not open for further replies.

lkincer

Electrical
May 19, 2003
5
I'm working on the specification for a 161/69/13.2 kV, 36/48/60 MVA, autotransformer with a loaded delta tertiary and a zig-zag grounding transformer downstream of the tertiary. The HV and LV windings are wye connected and solidly grounded. I'm specifying the tertiary winding with a 110 kV BIL and an arrester rating of 10 kV duty cycle or 8.4 kV MCOV. I've seen some utilities use an arrester rated 15 kV or 18 kV duty cycle on a similar unit. Has anyone worked on a similar design? Thanks for your help.
 
Replies continue below

Recommended for you

If you didn't have the grounding transformer, you'd use the 15 kV or 18 kV duty cycle rating.

With the grounding transformer, a 10 kV rating can be used.
 
10kV is enough if grounding transformer is sized for effectivelly grounded 13.2 kV system
 
Could the tertiary be energized without the grounding transformer connected? If so, use the higher rating.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor