Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Surge Arrester Ratings 1

Status
Not open for further replies.

wesles24

Electrical
Apr 13, 2015
29
0
0
US
Hello,
Need to know what surge arrester rating to apply to a 2.4kV winding on a transformer. So would the duty cycle rating be 1.38kV (2.4kV/sqrt3)well a little higher than operating voltage say 3kV or 6kV duty? And would the MCOV rating be 2.55kV or 5.1kV???

thanks,
not used to lower voltages
 
Replies continue below

Recommended for you

If solidly grounded then the arrestor needs some margin above the 1.38kV value. If it was ungrounded, then you'd be basing it on the full 2.4kV.

With the solidly grounded system a fault on one phase doesn't raise the voltage to ground on the others, but on an ungrounded (capacitively grounded) system a fault on one phase will cause the phase to ground voltage on the other phases to approach the phase-phase voltage.
 
Status
Not open for further replies.
Back
Top