coppabox
Electrical
- Jul 31, 2002
- 5
Hello,
I am seeking guidance on when and where to use cable surge arresters for buried 33kV cable.
The situation is as follows:
1. The HV cable is buried for its entire length except at each end where it is fully enclosed inside a switchroom. There is no exposure to a direct lightning strike (also see point 2 below)
2. The cable is buried at depth of 1m. There are many steel structures on the surface. Hence we are not considering a direct lightning strike to the cable through the 1m depth of soil (statistically its too low to consider).
3. There is no bare earth conductor above or near the HV cable. The HV cable screen is bonded both ends.
4. The terminations are via C-type connectors, these can be fitted with 5kA (or 10kA) surge arrester units
5. The cable lengths are very long, up to 6000m.
6. The switchboard vendor does not mandate that surge arresters are used at the cable terminations.
I am struggling to find a criteria and/or calculation method, to determine if the cable or connected equipment impulse rating will be exceeded due to an indirect lightning strike propagating via the buried cable.
Generally speaking, where HV cables are not exposed to direct lighting strikes, I see people add lighting surge arrester units to the 33kV switchboard termination but they cant really explain why.
If someone can point me to a simple criteria and/or calculation method it would be very much appreciated. Also, because the cable lengths are long, I am seeking guidance on whether when surge arresters would be required at both ends.
Regards,
Chris
I am seeking guidance on when and where to use cable surge arresters for buried 33kV cable.
The situation is as follows:
1. The HV cable is buried for its entire length except at each end where it is fully enclosed inside a switchroom. There is no exposure to a direct lightning strike (also see point 2 below)
2. The cable is buried at depth of 1m. There are many steel structures on the surface. Hence we are not considering a direct lightning strike to the cable through the 1m depth of soil (statistically its too low to consider).
3. There is no bare earth conductor above or near the HV cable. The HV cable screen is bonded both ends.
4. The terminations are via C-type connectors, these can be fitted with 5kA (or 10kA) surge arrester units
5. The cable lengths are very long, up to 6000m.
6. The switchboard vendor does not mandate that surge arresters are used at the cable terminations.
I am struggling to find a criteria and/or calculation method, to determine if the cable or connected equipment impulse rating will be exceeded due to an indirect lightning strike propagating via the buried cable.
Generally speaking, where HV cables are not exposed to direct lighting strikes, I see people add lighting surge arrester units to the 33kV switchboard termination but they cant really explain why.
If someone can point me to a simple criteria and/or calculation method it would be very much appreciated. Also, because the cable lengths are long, I am seeking guidance on whether when surge arresters would be required at both ends.
Regards,
Chris