Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Surge Supressor Downconductor Through the Classified Hazardous Area

Status
Not open for further replies.

pristava

Industrial
Jan 8, 2004
53
Surge Supressor 2/0 downconductor to be installed as suggested has to go through the Hazardous Area.
Surge Supressor, (connected with radio antenna) is on the top of the construction (unclassified area) but lower levels are Hazardous Areas Zone 2 because of heavy flammable gases.
I said on the meeting that is not acceptable, but Menager says that must be installed.
 
Replies continue below

Recommended for you

Generally,I am trying to find solution. That one doesn't work.
 
Hi Pristava,

Tough choices. I have never run into the need to intentionally run conductors designed to carry lightning current thru a hazardous area. Even insulated and within rigid conduit, voltage levels can spike up high enough to cause an arc to a nearby piece of grounded structure (perhaps the steel that the conduit might be clamped to).

I'd consult with the local electrical inspector, see if he (or she) would allow it under any conditions...

Let us know what you find out!

Old Dave
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor