How can I do a Manual Surge Test?,The growler tester could help me?
 
Replies continue below

Recommended for you

Growler tester will check only the short circuit [between turns or to Ground] of an armature. Surge tester will check the insulation
state between turns[rotor and stator].It is more complex and needs an oscilloscope.
 
Growler test might be able to locate short between turns, but only a pre existing dead short...because it's a low voltage test.

In contrast, surge test is a high voltage test, capable of breaking down weak turn insulation to detect it before it breaks down during power system-created surge or mechanical factors in service.

Said another way, surge testing is like a hipot for turn insulation. That can be good because it's sensitive. It also means the test should be planed and considered carefully before performing I it...and only done by qualified people

=====================================
(2B)+(2B)' ?
 