BSVBD
Structural
- Jul 23, 2015
- 463
Designing a cold production and storage facility.
The Production Room inside the facility is to have a walkable insulated ceiling, suspended and supported by the roof Open Web Steel Joist (OWSJ) bottom chords.
One supplier said the live load could be 20 PSF. When i asked where he got that load information from, he said the code book. I don't see this anywhere in IBC.
One manufacturer said 30 PSF.
I intended to use 40 PSF for catwalks, per code, but, then the supplier stated that would be MUCH more expensive.
(For IBC 2009 Live Load Table 1607.1, please see attached...)
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1481044100/tips/LL2009_uvnije.pdf[/url]
In IBC 2009, what exactly does "Primary roof members, exposed to a work floor" mean? This walkable ceiling is intended for equipment maintenance, thus, could be construed as a "work floor". Could i justify this 20 PSF for a walkable ceiling?
Any suggestions on how i could justify 20 psf? Other suggestions?
Thank you!
The Production Room inside the facility is to have a walkable insulated ceiling, suspended and supported by the roof Open Web Steel Joist (OWSJ) bottom chords.
One supplier said the live load could be 20 PSF. When i asked where he got that load information from, he said the code book. I don't see this anywhere in IBC.
One manufacturer said 30 PSF.
I intended to use 40 PSF for catwalks, per code, but, then the supplier stated that would be MUCH more expensive.
(For IBC 2009 Live Load Table 1607.1, please see attached...)
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1481044100/tips/LL2009_uvnije.pdf[/url]
In IBC 2009, what exactly does "Primary roof members, exposed to a work floor" mean? This walkable ceiling is intended for equipment maintenance, thus, could be construed as a "work floor". Could i justify this 20 PSF for a walkable ceiling?
Any suggestions on how i could justify 20 psf? Other suggestions?
Thank you!