electricpete
Electrical
- May 4, 2001
- 16,774
We replaced a “stabilized shunt” dc motor.
From what I can tell we have parallel field winding (F1 and F2) connected accross the input voltage.
We also have armature (A1 and A2) in series with Shunt/Stabilizing winding (S1 and S2). Diagram as follows
[tt]
L1========Arm===StabShunt======L2
| |
| |
=======Field ============[/tt]
We wired replacement motor same as original, started it up and it rotated backwards.
Our electricians swapped A1 and A2 to change direction of rotation. Then immediately after closing breaker but BEFORE closing contactor we got a ground on our dc bus and I was called in to take a look. I don’t think the wiring has any relationship to the ground (there is some moisture present and also one lead touching the term box cover with what appears to be a scrape in the tape at point of contact). But I want to verify the wiring. Off the top of my head I’m not comfortable swapping either of the series items individually since that disrupts their polarity relative to each other... would rather swap both series items together or else swap the field leads F1 and F2. I’ll be digging around for some more info, but I figured I’d ask here as well.
Question: Do you think it is ok to swap A1/A2 to reverse direction, or is it preferable to swap F1 and F2?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
From what I can tell we have parallel field winding (F1 and F2) connected accross the input voltage.
We also have armature (A1 and A2) in series with Shunt/Stabilizing winding (S1 and S2). Diagram as follows
[tt]
L1========Arm===StabShunt======L2
| |
| |
=======Field ============[/tt]
We wired replacement motor same as original, started it up and it rotated backwards.
Our electricians swapped A1 and A2 to change direction of rotation. Then immediately after closing breaker but BEFORE closing contactor we got a ground on our dc bus and I was called in to take a look. I don’t think the wiring has any relationship to the ground (there is some moisture present and also one lead touching the term box cover with what appears to be a scrape in the tape at point of contact). But I want to verify the wiring. Off the top of my head I’m not comfortable swapping either of the series items individually since that disrupts their polarity relative to each other... would rather swap both series items together or else swap the field leads F1 and F2. I’ll be digging around for some more info, but I figured I’d ask here as well.
Question: Do you think it is ok to swap A1/A2 to reverse direction, or is it preferable to swap F1 and F2?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.