SWER vs HVDS systems in Power Distribution
itsEEE
Student
May 23, 2024
7
Hey everyone,
I just wanted to know that what are the differences between the power system principles between a High Voltage Distribution System (HVDS) where a single-phase transformer 11Kv/440V is used, and a Single Wire Earth Return system (SWER). Are these the same and only differ in the application or something else is there?
Following is the image of SWER
In practice you may find that the isolating transformer is actually a step down transformer stepping down from a higher transmission voltage.
That is a common arrangement where I used to live.
That is; A transformer stepping down from transmission voltage to feed an SWER for distribution.
I suggest that an isolating transformer may be used to solve occasional local issues.
One possibility is that the isolating transformer, be it 1:1 or some other ratio will limit the Available Short Circuit Current on the SWER system.
This may be a safety issue.
The higher the ASCC on an SWER system, the higher voltage and the greater area of touch and step potentials in the event of a ground fault.
Ohm's law
Not just a good idea;
It's the LAW!
Thank you @waross for your valuable input, but still I am a little bit confused with SWER and HVDS systems. Are they same or they have any differences?
In the area that I am familiar with, transmission is generally at over 100kV.
The substation or "isolating" transformers step down to 35kV or less (11kV in your example) for distribution and reduce the ASCC.
Ohm's law
It's the LAW!
Thank you :)
Others are open to share their views.
SNTdon