Lyle,
Yes, in Canada PC computers have 15A 120V plugs that are served by 15A 120V receptacles a North American type configuration of live, neutral and ground that are connected to 15A single pole breakers in 120/208V 3ph 4w or sometimes 120/240V 1ph 3w electrical panels.
As per the name plate readings of the majority of office PCs, they usually draw about 300 Watts, or 2.5A at 120V.
In Canada the breakers are sized to protect the receptacles ... hence 15A receptacles are protected by 15A breakers, etc. Note in the US they use 20A 115V receptacles and 20A breakers for most equipment.
So for a standard office layout, I usually connect the receptacles for the PCs at 4 work stations together in parallel and then to the breaker, as breakers for this type of load can be loaded to 80%.
It used to be that PC manufacturers recommended that isolated grounding type receptacles be used for PCs, but they don't seem to require that as much any more, because they claim that there is better protection within the computers now. Note, I still circuit computers with IG receptacles, because the handy orange colour makes instructions to clients a tad simpler.... especially the don't plug your fan into any orange receptacles whatever.
Isolated grounding type receptacles have a separate ground wire for each circuit that runs from the ground slot in the receptacle back to an isolated ground bar in the electrical panel. As per the Canadian Electrical code the wiring for a 15A breaker can be no. 14, but no. 12 minimum is standard for larger projects and no. 10 wiring ends up being used for long runs due to voltage drop.
Any ways for the circuit loading... I have heard some people ..... not engineering type people.... claim that you can connect 6, or 8 PCs to a 15A breaker, but they seem to think that this is acceptable becauses PCs rarely work at their name plate readings... but I have spoken to systems analysts who say that it is for the best to go with the name plate readings.
Also, even if the name plate readings are less the 300W, the switching power suplies and stuff in the PCs will often place current on the neutral, so my understanding of good practice is 4 PCs per circuit, or an over sized neutral.
Margaret