Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations Toost on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Switchboard vs Distribution Panel 1

Status
Not open for further replies.

waldo321

Industrial
Aug 28, 2007
2
what's the difference between a switchboard and a distribution panel?

thanks.

Lee
 
Replies continue below

Recommended for you

Size and arrangement. Look at Switchboards and Panelboards in a manufacturer's catalog. Individual sections of switchboards are sometime referred to as panels, but probably not correctly.
 
One of the old original differences was that a switchboard was the term used when the back was accessible, whereas it is a panel when it is mounted against the wall. This general difference is probably not accurate anymore, though.
 
Another way to look at it is a switchboard is floor-mounted, while a panelboard is wall-mounted (although very large ones might reach the floor). One other criteria that we use is up to 1200 amps - panelboard - 1600 amp and above is a switchboard.
 
yes - confusing.

my next question will be what's the difference between a switchgear and a switchboard? That is sure to start a fight.
 
Been discussed ad nauseum in the Switchgear forum, this is the most recent:
thread279-155576
 
The terms switchboard and distribution panel are basically interchangeable today. At one point we used "switchboard" when it contained a series of fusible switches feeding loads and "distribution panel" when it contained circuit breakers. "Switchgear" is a general term which includes both of these as well as say, panelboards, motor control centers, unitized substations, etc....
 
Jamie,
As for switchgear, take a look a jraef's link. Switchgear has a very specific UL and ANSI definition and should not be confused with switchboards or panelboards.
 
Switchboards have different construction requirements that a distribution panelboard....Any panelboard can be called a "distribution panelboard if it has less than 10% of its OCP's serving 120 volt loads. In addition a switchboard can have both vertical and horizontal bussing. vertical bussing. the switchboard bussing ampacity can be tapered based on its designed load and other criteria
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor