Hi all,
I was curious as to what various utilities were doing as standard practice for synchronising in transmission systems.
At our older substations, we would typically have a single synchroniser with relays switching in the appropriate VT's and close coils. SCADA would issue a brief pulse, latching in the synchronising circuit for a predetermined time, with the circuit being interrupted when the circuit breaker closed, or if a trip command was issued from any source.
In our new substations, we are getting designs from consultants that require a latched close command from the SCADA system, and simply have a permissive in one of the protection relays which will allow the close command through once the two systems are near enough to synchronism. The SCADA command is latched for several minutes, and isn't unlatched by anything other than the timer.
What are people's views on the use of a single device for synchronising? (one blown VT fuse is all it would take for a disaster "dead-bus" close, for example). In generating stations (where I have more experience), the standard we would apply is minimum two devices for synchronising, taken from different phases. This would generally be either the auto-synchroniser OR the operator (when manual closing), in conjunction with suitable sync check relays.
Any thoughts on the latched close signal from SCADA? I don't like the idea of a signal remaining latched in, and I especially don't like the idea of it not being interrupted by a trip command, other than by the CB anti-pump circuit.
I was curious as to what various utilities were doing as standard practice for synchronising in transmission systems.
At our older substations, we would typically have a single synchroniser with relays switching in the appropriate VT's and close coils. SCADA would issue a brief pulse, latching in the synchronising circuit for a predetermined time, with the circuit being interrupted when the circuit breaker closed, or if a trip command was issued from any source.
In our new substations, we are getting designs from consultants that require a latched close command from the SCADA system, and simply have a permissive in one of the protection relays which will allow the close command through once the two systems are near enough to synchronism. The SCADA command is latched for several minutes, and isn't unlatched by anything other than the timer.
What are people's views on the use of a single device for synchronising? (one blown VT fuse is all it would take for a disaster "dead-bus" close, for example). In generating stations (where I have more experience), the standard we would apply is minimum two devices for synchronising, taken from different phases. This would generally be either the auto-synchroniser OR the operator (when manual closing), in conjunction with suitable sync check relays.
Any thoughts on the latched close signal from SCADA? I don't like the idea of a signal remaining latched in, and I especially don't like the idea of it not being interrupted by a trip command, other than by the CB anti-pump circuit.