synchronous generator exciter cct

Status
Not open for further replies.

adapter3

Electrical
Joined
Mar 10, 2004
Messages
2
Location
CA
Can someone give me a refresher here.......my usual is 600V and below

how does this work? Whats does the exciter cct control...phase angle and voltage output?

any input would be appreciated


adapter3
 
It depends. There are rotating exciters and static exciters with slip rings. There are also exciters with a static exciter that feeds a rotating transformer with rotating rectifiers and sometimes a circuit that shorts the rectifiers during start. In the latter case, the rotor winding is used as an asynchronous starting winding which is shorted by the thyristors that are part of the rotating rectifier.

So, there are a great many options. But most of them - I would say all - use thyristors to control excitation. The thyristors are phase controlled. A long delay before they are fired gives a low excitation and a short delay produces more voltage and hence more current in the excitation winding. The delay is counted in electric degrees. One cycle is 360 degrees so normal delay is between 30 and 150 degrees (with some exceptions).

Have a look at the Basler site . A lot to read there.

Gunnar Englund
 