burntcoil
Electrical
- Sep 28, 2011
- 75
We have a 27000HP Synchronous motor operating at 13.2kV. The motor excitation control panel have redundant DESC200 Excititation Controller from Basler. During normal operation, if the Master fails, the excitation control will automatically transfer to backup controller. The motor was tripped on Loss of Excitation (although exciter circuit was checked and found healthy). When the motor was started with backup conrtoller, its working fine. After the startup when we shifted the motor to master controller, it tripped again. Now the motor is on backup controller. I am interested to know if we can test the Master to Backup and Backup to Master transfer without running the motor? Do anyone have such previous experience?