I have asked this question to many folks before. And I always believe solidly of the grounding principles in NEC. I recently found myself in doubt whether system grounding and equipment grounding should be connected together, which shows how poorly I understand this subject.
Recently we installed a new X-Ray machine in a clinic. This is a 400V unit supplied by a brand new 150kVA, 6.6kV-420V, 3 ph 4W, delta-wye transformer. The transformer is co-located together with 2 other 300kVA, 6.6kV-208/120V, 3ph 4W, and 150kVA 6.6kV-400V, 3ph 3W(center tap) within an enclosure (substation).
The equipment manufacturer insisted that X-Ray equipment be supplied with a separate grounding electrode dedicated for the X-Ray control cabinet, which is separate from the system grounidng at the substation. (At the substation, all the transformer shared a common ground.)
Although I mentioned that the separate X-Ray grounding electrodes (Equipment ground purpose) should be tied in with the service ground at the service disconnect (System ground purpose), per NEC 250-2, the equipment manufacturer voted against and directed only separate ground be used.
We are located in Japan, the grounding concept is different than in US.
I was explained by a local Japanese engineer that because we are dealing with different voltage system, the grounding at the substation should not be tied together and should be kept separate. And because System ground and Equipment ground serves entirely different purposes, they should remain separate. The reason is when there is a fault at one of the phases, the grounding conductor serving as a ground fault return path will carry a different potential and damage the equipment should they be connected at the source.
I would like to get some advice on this. I am very confused.
Recently we installed a new X-Ray machine in a clinic. This is a 400V unit supplied by a brand new 150kVA, 6.6kV-420V, 3 ph 4W, delta-wye transformer. The transformer is co-located together with 2 other 300kVA, 6.6kV-208/120V, 3ph 4W, and 150kVA 6.6kV-400V, 3ph 3W(center tap) within an enclosure (substation).
The equipment manufacturer insisted that X-Ray equipment be supplied with a separate grounding electrode dedicated for the X-Ray control cabinet, which is separate from the system grounidng at the substation. (At the substation, all the transformer shared a common ground.)
Although I mentioned that the separate X-Ray grounding electrodes (Equipment ground purpose) should be tied in with the service ground at the service disconnect (System ground purpose), per NEC 250-2, the equipment manufacturer voted against and directed only separate ground be used.
We are located in Japan, the grounding concept is different than in US.
I was explained by a local Japanese engineer that because we are dealing with different voltage system, the grounding at the substation should not be tied together and should be kept separate. And because System ground and Equipment ground serves entirely different purposes, they should remain separate. The reason is when there is a fault at one of the phases, the grounding conductor serving as a ground fault return path will carry a different potential and damage the equipment should they be connected at the source.
I would like to get some advice on this. I am very confused.