Good night experts.
I work for the utility in Madeira island. Our grid is small and not connected to Portugal mainland.
I want to validate our RoCoF figure. I have calculated all the synchronous generators (Si) inertia constants (Hi).
I´ve used Hi= (J*Wi^2)/(0.5*Si).
I´ve read somewhere that we should refer all the powers to, for example, 10 MVA.
So I have multiplied the final figures: Hifinal=(Si/10)*Hi.
I´m a newbie on the subject and I´m having problems with the system inertia constant (Hsys).
I have came across two formulas:
One formula multiplies the grid nominal frequency f0 and the other doesn´t. I don´t understand the difference.
The system inertia constant (Hsys) will be referred to the sum of all synchronous powers online.
But the individual Hi figures are 10 MVA based. Something is wrong.
What am I missing here?
All your help will be greatly appreciated.
Best regards.
Carlos Melim
I work for the utility in Madeira island. Our grid is small and not connected to Portugal mainland.
I want to validate our RoCoF figure. I have calculated all the synchronous generators (Si) inertia constants (Hi).
I´ve used Hi= (J*Wi^2)/(0.5*Si).
I´ve read somewhere that we should refer all the powers to, for example, 10 MVA.
So I have multiplied the final figures: Hifinal=(Si/10)*Hi.
I´m a newbie on the subject and I´m having problems with the system inertia constant (Hsys).
I have came across two formulas:


One formula multiplies the grid nominal frequency f0 and the other doesn´t. I don´t understand the difference.
The system inertia constant (Hsys) will be referred to the sum of all synchronous powers online.
But the individual Hi figures are 10 MVA based. Something is wrong.
What am I missing here?
All your help will be greatly appreciated.
Best regards.
Carlos Melim