stevenal
Electrical
- Aug 20, 2001
- 3,824
My interest is from the utility side. The NESC proposals for 2007 include arc flash protection requirements. Similar rules are being considered by OSHA. The rules themselves are pretty simple, assigning caloric clothing values to incident energy levels or to tabulated fault currents and clearing times. No more guidance is offered, leaving us with IEEE 1584 for details. Regarding clearing time, by my reading, 1584 says to look at the first upstream device from the possible arc flash location. Contrasting this procedure with system protection leaves me somewhat puzzled. We try to set primary and backup protection both to protect the system. Both secondary and primary side protection on a transformer, for example, lie beneath the transformer damage curve. Likewise for line protection. Whether backup is local and triggered by breaker failure or is remote and coordinated, backup protection clears a fault before the line burns down. So I'm left with the uncomfortable proposition that the equipment is more important than the safety of the workers. Sorta goes against the engineering code of ethics. Any comments on this observation? Thanks.