redtrumpet
Electrical
- Mar 29, 2001
- 323
I had mentioned in a previous post that I have a client who has several 63 kV - 13.8 kV delta-wye ANSI Group 2 transformers. Some of these transformers have A-B-C sequence on the primary, some have A-C-B. The client is attempting to parallel secondaries. Obviously, there is a problem with paralleling transformers with opposite primary sequences - a 60 degree phase shift is introduced between secondaries (30 lead on the A-C-B + 30 lag on the A-B-C = 60 degrees).
The client has made some changes to cable secondaries to at least get proper rotation when doing a cold transfer, realizing a parallel (hot) transfer is not feasible right now. Voltage measurements were taken across the line and load terminals of two open tie breakers involving three transformers.
Based on visual inspection of the primary connections and the transformer nameplates, the transformers appear to be connected H1-H2-H3 as follows:
T1 - B-C-A primary, 30 degree lag on secondary
T2 - C-B-A primary, 30 degree lead on secondary
T3 - A-B-C primary, 30 degree lag on secondary
For convenience designate the two systems a-b-c and a'-b'-c' read left-to-right at the back of the 13.8 kV switchgear breaker cell, recognizing a and a' may not necessarily correspond to the X1 transformer bushing. Measurements were as follows:
T2-T3
Va-b = 12.94 kV
Vb-c = 12.88 kV
Vc-a = 13.29 kV
Va'-b'= 13.45 kV
Vb'-c' = 13.50 kV
Vc'-a' = 13.85 kV
So far, so good - line-to-line voltages read between phases as expected.
Va-a' = 7.75 kV
Va-b' = 15.60 kV
Va-c' = 7.75 kV
Vb-a' = 7.70 kV
Vb-b' = 7.77 kV
Vb-c' = 15.54 kV
Vc-a' = 15.54 kV
Vc-b' = 7.07 kV
Vc-c' = 7.82 kV
Based on these measurements, the roughly line-to-neutral voltages correspond to a 60 degree shift, and the roughly twice line-to-neutral voltages correspond to 180 degree shifts. From this I inferred that the systems are rotating in the same direction, and that a-a', b-b' and c-c' are 60 degrees apart. This matched my expectation based on the primary connections of T2 and T3. It appears the A and C cable leads of one side of the tie were swapped to correct the secondary rotation.
However, a set of voltages measured across the tie breaker connecting T1 and T3 has me stumped.
T1-T3
Va-b = 12.95 kV
Vb-c = 12.95 kV
Vc-a = 12.87 kV
Va'-b'= 12.78 kV
Vb'-c' = 12.78 kV
Vc'-a' = 12.65 kV
Again, line-to-line voltages read between phases as expected.
Va-a' = 13.22 kV
Va-b' = 7.82 kV
Va-c' = 7.66 kV
Vb-a' = 7.10 kV
Vb-b' = 13.22 kV
Vb-c' = 7.82 kV
Vc-a' = 8.38 kV
Vc-b' = 7.11 kV
Vc-c' = 13.22 kV
Now, it appears that there is a 120 degree shift between phases based on a-a', b-b', and c-c' readings. However, the line-to-neutral voltage readings indicate a 60 degree shift - an impossible situation to resolve in my mind. Based on primary connections, these two systems should both be A-B-C rotation and exhibit either 0 or 120 degree phase shifts.
I was not present during the voltage testing. Am I missing something obvious here, or do the second set of voltage readings appear inconsistent? I want a second opinion before I approach the client about redoing the measurements.
The client has made some changes to cable secondaries to at least get proper rotation when doing a cold transfer, realizing a parallel (hot) transfer is not feasible right now. Voltage measurements were taken across the line and load terminals of two open tie breakers involving three transformers.
Based on visual inspection of the primary connections and the transformer nameplates, the transformers appear to be connected H1-H2-H3 as follows:
T1 - B-C-A primary, 30 degree lag on secondary
T2 - C-B-A primary, 30 degree lead on secondary
T3 - A-B-C primary, 30 degree lag on secondary
For convenience designate the two systems a-b-c and a'-b'-c' read left-to-right at the back of the 13.8 kV switchgear breaker cell, recognizing a and a' may not necessarily correspond to the X1 transformer bushing. Measurements were as follows:
T2-T3
Va-b = 12.94 kV
Vb-c = 12.88 kV
Vc-a = 13.29 kV
Va'-b'= 13.45 kV
Vb'-c' = 13.50 kV
Vc'-a' = 13.85 kV
So far, so good - line-to-line voltages read between phases as expected.
Va-a' = 7.75 kV
Va-b' = 15.60 kV
Va-c' = 7.75 kV
Vb-a' = 7.70 kV
Vb-b' = 7.77 kV
Vb-c' = 15.54 kV
Vc-a' = 15.54 kV
Vc-b' = 7.07 kV
Vc-c' = 7.82 kV
Based on these measurements, the roughly line-to-neutral voltages correspond to a 60 degree shift, and the roughly twice line-to-neutral voltages correspond to 180 degree shifts. From this I inferred that the systems are rotating in the same direction, and that a-a', b-b' and c-c' are 60 degrees apart. This matched my expectation based on the primary connections of T2 and T3. It appears the A and C cable leads of one side of the tie were swapped to correct the secondary rotation.
However, a set of voltages measured across the tie breaker connecting T1 and T3 has me stumped.
T1-T3
Va-b = 12.95 kV
Vb-c = 12.95 kV
Vc-a = 12.87 kV
Va'-b'= 12.78 kV
Vb'-c' = 12.78 kV
Vc'-a' = 12.65 kV
Again, line-to-line voltages read between phases as expected.
Va-a' = 13.22 kV
Va-b' = 7.82 kV
Va-c' = 7.66 kV
Vb-a' = 7.10 kV
Vb-b' = 13.22 kV
Vb-c' = 7.82 kV
Vc-a' = 8.38 kV
Vc-b' = 7.11 kV
Vc-c' = 13.22 kV
Now, it appears that there is a 120 degree shift between phases based on a-a', b-b', and c-c' readings. However, the line-to-neutral voltage readings indicate a 60 degree shift - an impossible situation to resolve in my mind. Based on primary connections, these two systems should both be A-B-C rotation and exhibit either 0 or 120 degree phase shifts.
I was not present during the voltage testing. Am I missing something obvious here, or do the second set of voltage readings appear inconsistent? I want a second opinion before I approach the client about redoing the measurements.