- Nov 27, 2009
- 4
Hi
I am stuck offshore without my complete library and very poor and intermittent bandwidth - can anyone tell me is there any guidance in IEC 61892-2 about installed generation capacity and system voltage selection?
NORSOK E-001 reccomends no more than 4MW at 690VAC.
Would you believe there is 15MW at 690VAC ? I think the shipyard must have had shares in a copper mine - I have never seen cables so big, and the operating current is 10000 amps and seems to be playing havoc with the instrumentation.
AnythingWithAWire
I am stuck offshore without my complete library and very poor and intermittent bandwidth - can anyone tell me is there any guidance in IEC 61892-2 about installed generation capacity and system voltage selection?
NORSOK E-001 reccomends no more than 4MW at 690VAC.
Would you believe there is 15MW at 690VAC ? I think the shipyard must have had shares in a copper mine - I have never seen cables so big, and the operating current is 10000 amps and seems to be playing havoc with the instrumentation.