I'm trying to determine the zero sequence impedances for a T-model of a step down transformer so that I can perform phase to ground short circuit current calculations on the low voltage side of the transformer but i don't understand the H-L%, H-T% and L-T% format that the manufacturer supplied as shown below.
Here are the technical details on step down transformer provided by the manufacturer:
21/28/35 MVA ONAN/ONAF/ONAF
Vector group: YNyn0d1
Winding Type: Core
138 kV Grounded Wye High Side
4.16 kV Tertiary Delta
12.0 kV Grounded-Wye Low Side
Guaranteed positive sequence impedances, H-L% = 7.0
Z1 on rated MVA base, at 85°C H-T% = 10.66
and mid tap L-T% = 2.36
Guaranteed zero sequence impedances, H-L% = 6.15
Z0 on rated MVA base, at 85°C H-T% = 8.68
and mid tap L-T% = 2.53
Here are the technical details on step down transformer provided by the manufacturer:
21/28/35 MVA ONAN/ONAF/ONAF
Vector group: YNyn0d1
Winding Type: Core
138 kV Grounded Wye High Side
4.16 kV Tertiary Delta
12.0 kV Grounded-Wye Low Side
Guaranteed positive sequence impedances, H-L% = 7.0
Z1 on rated MVA base, at 85°C H-T% = 10.66
and mid tap L-T% = 2.36
Guaranteed zero sequence impedances, H-L% = 6.15
Z0 on rated MVA base, at 85°C H-T% = 8.68
and mid tap L-T% = 2.53