birddogger
Electrical
- Feb 23, 2004
- 31
If a 13.8kV-480/277 2500 kVA AA/FA transformer is placed facing the 277/480V, 2500A switchboard it serves, does condition 2 or 3 of Table 110.26(A)(1) apply? Since a transformer is never worked on live, I would think the enclosure could be considered grounded and thus it would fall under condition 2 instead of 3. I’m trying to find out if the working space between the two pieces of equip. could be reduced from 4 ft. to 3 ft. because of this.
If the transformer is indeed considered live, then does it actually qualify as over 600V since the primary is at 13.8kV, and thus I would have to have 9 ft. working space (per Table 110.34(A)) between it and the front of the switchboard? If that’s the case, I’m in trouble.
Also, regarding an overhead feeder busduct betweem the two - is this realistic, to try to land 5 sets of #500 between the busduct flange and the bus terminals on both sides of the duct without extra bending space? I would imagine that the cable bending radii might make this impossible without the use of a top hat or a separate pull section, in which case we might just go ahead and run conduit under the floor between the two, if there has to be a pull section either way.
If the transformer is indeed considered live, then does it actually qualify as over 600V since the primary is at 13.8kV, and thus I would have to have 9 ft. working space (per Table 110.34(A)) between it and the front of the switchboard? If that’s the case, I’m in trouble.
Also, regarding an overhead feeder busduct betweem the two - is this realistic, to try to land 5 sets of #500 between the busduct flange and the bus terminals on both sides of the duct without extra bending space? I would imagine that the cable bending radii might make this impossible without the use of a top hat or a separate pull section, in which case we might just go ahead and run conduit under the floor between the two, if there has to be a pull section either way.