In the "pole barn" industry, we depend very heavily on metal-clad roof and wall diaphragms. For those not familiar with this method of construction, we use mechanically laminated dimensional lumber columns in the ground typically 8' o.c. Wood trusses are typically 8' o.c. as well. The framing on the roof then is 2x4 purlins (on edge) and on the walls it is 2x4's flat. Corrugated steel panels are screwed to this wood framing to provide a diaphragm assembly.
An associate and I were having a discussion about whether or not we can take the tabular shear values of tested diaphragm assemblies and increase their capacity by a 4/3 or 1.6 factor. I'm kind of torn. I read a thread about the 4/3 factor, but I believe that is more of a reduction in loads due to the likelihood of a combination of two or more events happening simultaneously. Chap 16 of the IBC states clearly that "increases in allowable stresses specified in the appropriate materials section of this code or referenced standard shall not be used with the load combinations of Section 1605.3.1 (IBC 2000) except that duration of load increase shall be permitted in accordance with Chap 23."
The IBC does not publish steel-clad diaphragms like it does wood sheathing clad diaphragms, but does reference a standard called Diaphragm Design of Metal-Clad, Post-Frame Rectangular buildings. Nowhere in that document does it give any values or state that tabular diaphragm values from tested assemblies may or may not be increased.
For wood-on-wood diaphragms, the IBC permits a 40% increase in tabular values for wind design. Does it seem reasonable that since the metal-cladding is attached to wood framing that I can use the load duration factors for wood design (NDS), or 1.4 like the IBC allows for wood panel diaphragms, or even a 1.33 increase? Any thoughts would be appreciated.
Thank you.
An associate and I were having a discussion about whether or not we can take the tabular shear values of tested diaphragm assemblies and increase their capacity by a 4/3 or 1.6 factor. I'm kind of torn. I read a thread about the 4/3 factor, but I believe that is more of a reduction in loads due to the likelihood of a combination of two or more events happening simultaneously. Chap 16 of the IBC states clearly that "increases in allowable stresses specified in the appropriate materials section of this code or referenced standard shall not be used with the load combinations of Section 1605.3.1 (IBC 2000) except that duration of load increase shall be permitted in accordance with Chap 23."
The IBC does not publish steel-clad diaphragms like it does wood sheathing clad diaphragms, but does reference a standard called Diaphragm Design of Metal-Clad, Post-Frame Rectangular buildings. Nowhere in that document does it give any values or state that tabular diaphragm values from tested assemblies may or may not be increased.
For wood-on-wood diaphragms, the IBC permits a 40% increase in tabular values for wind design. Does it seem reasonable that since the metal-cladding is attached to wood framing that I can use the load duration factors for wood design (NDS), or 1.4 like the IBC allows for wood panel diaphragms, or even a 1.33 increase? Any thoughts would be appreciated.
Thank you.