Tank, Vessel on foundation Anchor, Concrete Design with Overstrength factor (ACI 318-14, ASCE 7-16)
I believe that there are many previous post on this issue.
However, I would like to get other engineer's opinions.
Here in after I will use "ACI" for ACI 318-14, "ASCE" for ASCE 7-16.
To be clear, [Concrete] [Steel] will be noted.
Design condition considered as below :
Seismic design category D
Pre-installed type anchor bolt used.
Tank or Vessel supported on concrete pedestal or concrete foundation.
1. Regarding ASCE
1) ASCE Sec. 15.4.9.1
Anchor in concrete shall be designed by Chapter 17 of ACI.
2) ASCE Sec. 15.7.3 a.
2.1) Anchor bolt[STEEL] embedded in concrete shall be designed by Sec. 15.7.5
ASCE Sec. 15.7.5 special detailing requirements
(1) Anchor bolt(STEEL) shall have minimum 8*diameter gauge length.
(2) Anchor bolt(STEEL) shall be designed(sized) without overstrength factor.
2.2) Connections[STEEL & CONCRETE] shall be designed to develop Ωo(Overstrength Factor) * Design force or Actual required strength of the anchor in tension calculated by referece document
Let's only consider that Overstrength Factor to be used.
3) Notation
- Anchor Bolt[STEEL] means "Pre-installed Anchor bolt"
- Connections[STEEL] means "Base Plate" , "Anchor Chair Plates" and etc.
- Connections[CONCRETE] means "Concrete Pedestal" , "Concrete Foundation" and etc.
4) Summary as per ASCE 7-16, Section 15.7.3
- Anchor Bolt[STEEL] - it shall be designed(sized) by "not overstrength" factored seismic load.
- Connections[STEEL] = Base Plate, Anchor Chair Plates - it shall be designed by "overstrength" factored seismic load.
- Connections[CONCRETE in tension] = Strength(breakout, pullout, sideface blowout) - it shall be designed by "overstrength" factored seismic load.
- Connections[CONCRETE in shear] = Strength(breakout, pryout) - it shall be designed by "overstrength" factored seismic load.
- Connections[STEEL] = Anchor Reinforcement in concrete - it shall be designed by "overstrength" factored seismic load.
- The only element that shall be designed "without overstrength" factor is "Anchor Bolt[STEEL]"
Question 1) Do you(engineers) agreed with above conclusion?
2. Regarding ACI
1) ACI Section 17.2.3.4.3(tension) and 17.2.3.5.3(shear) require "shall satisfy "one" of options"
2) ACI Section 17.2.3.4.3 Tensile anchor
- Option a) - Same and more as per section 15.7.5 of ASCE 7-16
- Option d) - Overstrength factor
3) ACI Section 17.2.3.5.3 Shear anchor
- Option c) - Overstrength factor
4) ACI Section 17.2.3.4.3 Tensile anchor
With above conclusion regarding ASCE,
- Anchor Bolt[STEEL in tension] - only option a) shall be used.
- Connections[STEEL in tension] = Base plate, Anchor chair plates = only option d) shall be used.
- Connections[CONCRETE in tension] = Strength(breakout, pullout, sideface blowout) = only option d) shall be used.
- Connections[STEEL in tension] = Anchor Reinforcement in concrete = only option d) shall be used.
5) ACI Section 17.2.3.5.3 Shear anchor
With above conclusion regarding ASCE,
- Anchor Bolt[STEEL in shear] - there's no option? -> Only way is that shear shall not be occurred or overcomed.
- Connections[STEEL in shear] = Base plate, Anchor chair plates = only option c) shall be used.
- Connections[CONCRETE in shear] = Strength(breakout, pryout) = only option c) shall be used.
- Connections[STEEL in shear] = Anchor Reinforcement in concrete = only option c) shall be used.
Question 2) Tensile Anchor : With ASCE and ACI, it seems like the only possible way is "mixed design option" like above(Tension : Option a) and Option d)). Do you agreed with this?
Question 3) Shear Anchor : With ASCE and ACI, it seems like the only possible way is "Shear shall be not occured or overcomed by frction load from vertical load" like above. Do you agreed with this?
Thanks for any responses.
I believe that there are many previous post on this issue.
However, I would like to get other engineer's opinions.
Here in after I will use "ACI" for ACI 318-14, "ASCE" for ASCE 7-16.
To be clear, [Concrete] [Steel] will be noted.
Design condition considered as below :
Seismic design category D
Pre-installed type anchor bolt used.
Tank or Vessel supported on concrete pedestal or concrete foundation.
1. Regarding ASCE
1) ASCE Sec. 15.4.9.1
Anchor in concrete shall be designed by Chapter 17 of ACI.
2) ASCE Sec. 15.7.3 a.
2.1) Anchor bolt[STEEL] embedded in concrete shall be designed by Sec. 15.7.5
ASCE Sec. 15.7.5 special detailing requirements
(1) Anchor bolt(STEEL) shall have minimum 8*diameter gauge length.
(2) Anchor bolt(STEEL) shall be designed(sized) without overstrength factor.
2.2) Connections[STEEL & CONCRETE] shall be designed to develop Ωo(Overstrength Factor) * Design force or Actual required strength of the anchor in tension calculated by referece document
Let's only consider that Overstrength Factor to be used.
3) Notation
- Anchor Bolt[STEEL] means "Pre-installed Anchor bolt"
- Connections[STEEL] means "Base Plate" , "Anchor Chair Plates" and etc.
- Connections[CONCRETE] means "Concrete Pedestal" , "Concrete Foundation" and etc.
4) Summary as per ASCE 7-16, Section 15.7.3
- Anchor Bolt[STEEL] - it shall be designed(sized) by "not overstrength" factored seismic load.
- Connections[STEEL] = Base Plate, Anchor Chair Plates - it shall be designed by "overstrength" factored seismic load.
- Connections[CONCRETE in tension] = Strength(breakout, pullout, sideface blowout) - it shall be designed by "overstrength" factored seismic load.
- Connections[CONCRETE in shear] = Strength(breakout, pryout) - it shall be designed by "overstrength" factored seismic load.
- Connections[STEEL] = Anchor Reinforcement in concrete - it shall be designed by "overstrength" factored seismic load.
- The only element that shall be designed "without overstrength" factor is "Anchor Bolt[STEEL]"
Question 1) Do you(engineers) agreed with above conclusion?
2. Regarding ACI
1) ACI Section 17.2.3.4.3(tension) and 17.2.3.5.3(shear) require "shall satisfy "one" of options"
2) ACI Section 17.2.3.4.3 Tensile anchor
- Option a) - Same and more as per section 15.7.5 of ASCE 7-16
- Option d) - Overstrength factor
3) ACI Section 17.2.3.5.3 Shear anchor
- Option c) - Overstrength factor
4) ACI Section 17.2.3.4.3 Tensile anchor
With above conclusion regarding ASCE,
- Anchor Bolt[STEEL in tension] - only option a) shall be used.
- Connections[STEEL in tension] = Base plate, Anchor chair plates = only option d) shall be used.
- Connections[CONCRETE in tension] = Strength(breakout, pullout, sideface blowout) = only option d) shall be used.
- Connections[STEEL in tension] = Anchor Reinforcement in concrete = only option d) shall be used.
5) ACI Section 17.2.3.5.3 Shear anchor
With above conclusion regarding ASCE,
- Anchor Bolt[STEEL in shear] - there's no option? -> Only way is that shear shall not be occurred or overcomed.
- Connections[STEEL in shear] = Base plate, Anchor chair plates = only option c) shall be used.
- Connections[CONCRETE in shear] = Strength(breakout, pryout) = only option c) shall be used.
- Connections[STEEL in shear] = Anchor Reinforcement in concrete = only option c) shall be used.
Question 2) Tensile Anchor : With ASCE and ACI, it seems like the only possible way is "mixed design option" like above(Tension : Option a) and Option d)). Do you agreed with this?
Question 3) Shear Anchor : With ASCE and ACI, it seems like the only possible way is "Shear shall be not occured or overcomed by frction load from vertical load" like above. Do you agreed with this?
Thanks for any responses.