Hi everyone,
I am reviewing a modification to wastewater existing tank by adding a dividing wall, the tank is 29' x 29' 18' high and
the dividing wall is 18' from the side wall. The structural engineer submitted a structural calculation based on 11.5'
water depth using PCA tables using three side fixed wall and came up with 14" wall with # 6 @ 12" rebars verticaly and
horizontaly. When the depth mistake has been discovered, the calculation went back to him to revise it, he did not
change the design calculation, he just used a software bending digram using wall supports fixed on one side and hinged on
the other side with hinged support at the bottom and because this case is not listed on PCA tables, he is using the
software and that he design would stay the same. Please advise if you think the wall be structurally sound and stable.
I think it is underdesigned that way
I am reviewing a modification to wastewater existing tank by adding a dividing wall, the tank is 29' x 29' 18' high and
the dividing wall is 18' from the side wall. The structural engineer submitted a structural calculation based on 11.5'
water depth using PCA tables using three side fixed wall and came up with 14" wall with # 6 @ 12" rebars verticaly and
horizontaly. When the depth mistake has been discovered, the calculation went back to him to revise it, he did not
change the design calculation, he just used a software bending digram using wall supports fixed on one side and hinged on
the other side with hinged support at the bottom and because this case is not listed on PCA tables, he is using the
software and that he design would stay the same. Please advise if you think the wall be structurally sound and stable.
I think it is underdesigned that way