Gentlemen,
I previously posted a question regarding the tapping of branch panelboard feeders on an airport project we have under construction. The following issue was also raised by the Electrical Inspector, although in this case, I feel he may be mistaken, (difficult to convince an AHJ that they are ever mistaken, I know).
We have an existing indoor 12kV-480Y/277V,3ph,4w,4000A substation supplying the normal side feeds to several Automatic Transfer Switches. Unfortunately the 480V Distribution section is full and we needed to add a feeder for another ATS. The designer called for a new feeder to be tapped to the existing bus and routed to an enclosed 1600A/3P circuit breaker which feeds the Normal side of the new ATS.
The inspector has quoted the feeder tap section of the NEC 240-21(b)(2) because the tap conductors are 37ft in length which he states exceeds the 25ft maximum allowed by code.
My assertion is that this provision of the NEC is not applicable because we are not tapping a "feeder", we are making our connection at a switchboard. Furthermore, we are protecting the feeder with the circuit breaker and the feeder is contained within the electrical room. (There is really no other location in this extremely full electrical room to mount the breaker, (aside from the fact it is already installed)).
Does that argument have any validity in your opinions? I would be interested in hearing your views. Are there any Inspectors in the forum?
Thank you and regards,
EEJAIME
I previously posted a question regarding the tapping of branch panelboard feeders on an airport project we have under construction. The following issue was also raised by the Electrical Inspector, although in this case, I feel he may be mistaken, (difficult to convince an AHJ that they are ever mistaken, I know).
We have an existing indoor 12kV-480Y/277V,3ph,4w,4000A substation supplying the normal side feeds to several Automatic Transfer Switches. Unfortunately the 480V Distribution section is full and we needed to add a feeder for another ATS. The designer called for a new feeder to be tapped to the existing bus and routed to an enclosed 1600A/3P circuit breaker which feeds the Normal side of the new ATS.
The inspector has quoted the feeder tap section of the NEC 240-21(b)(2) because the tap conductors are 37ft in length which he states exceeds the 25ft maximum allowed by code.
My assertion is that this provision of the NEC is not applicable because we are not tapping a "feeder", we are making our connection at a switchboard. Furthermore, we are protecting the feeder with the circuit breaker and the feeder is contained within the electrical room. (There is really no other location in this extremely full electrical room to mount the breaker, (aside from the fact it is already installed)).
Does that argument have any validity in your opinions? I would be interested in hearing your views. Are there any Inspectors in the forum?
Thank you and regards,
EEJAIME