turtlepokerman
Electrical
- Jan 7, 2015
- 7
Greetings,
I have a 120Vac Control Cable that runs from a small 100VA 1-Ph CPT located in a MCC to a Relay Panel. Am I required to run a equipment grounding conductor within the cable to consider it TC-ER rated? There are numerous of these cables that are running between the two pieces of equipment.
The section that confuses me is NEC 2011 section 336.10(7) which states that "Equipment grounding for the utilization equipment shall be provided by an equipment grounding conductor within the cable.". Currently both the MCC and the panel are located in the same building and both equipment are bonded to the ground ring that is run within the building. So if a short occurs in the panel or the MCC the fault path would be through the building ground ring. All raceway is bonded to the ground ring as well, but the raceway is not continuously run along the conductor.
All help is appreciated!
I have a 120Vac Control Cable that runs from a small 100VA 1-Ph CPT located in a MCC to a Relay Panel. Am I required to run a equipment grounding conductor within the cable to consider it TC-ER rated? There are numerous of these cables that are running between the two pieces of equipment.
The section that confuses me is NEC 2011 section 336.10(7) which states that "Equipment grounding for the utilization equipment shall be provided by an equipment grounding conductor within the cable.". Currently both the MCC and the panel are located in the same building and both equipment are bonded to the ground ring that is run within the building. So if a short occurs in the panel or the MCC the fault path would be through the building ground ring. All raceway is bonded to the ground ring as well, but the raceway is not continuously run along the conductor.
All help is appreciated!