TCL & M D OF A TRANSFORMER

Status
Not open for further replies.

sarathkurian

Electrical
Aug 11, 2014
1
Hi
Can you tell me for a 1500kVA Distribution transformer how much be Total connected load (TCL) and Maximum Demand (M D).

Regards,
Sarath Kurian
 
Replies continue below

Recommended for you

If you mean maximum TCL and MD then it may depend on the ownership and operating guidelines, or it may depend on codes.
For a utility owned transformer the maximum demand may depend on the duration of the overload and the maximum allowable voltage dip. Loading above 100% leads to poorer voltage regulation and reduced transformer life.
If the transformer is subject to electrical codes then some codes require that the continuously connected load may not exceed 100% of the transformer rating and the maximum demand may not exceed 100% of the transformer rating. Under some conditions the maximums may be 80% of the ratings.
In North America most customer owned transformers are subject to the electrical codes.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 