Temperature Limit Switch Failure

Status
Not open for further replies.

JSong

Electrical
Dec 31, 2015
10
Hi all,

We had a temperature limit switch failure problem in a heat exchange fan control circuit. The fan is a 1/6 HP single phase motor, and it is controlled by a Honeywell 'BM-2R-A2' temperature limit switch. This limit switch is rated for 1/2 HP that shouldn't have any problem in a 1/6 HP case, but it kept failing and the contactor got welded. Does anyone have some insight regarding this? Would you think that adding a surge suppressor would help?

Thanks,
JS
 
Replies continue below

Recommended for you

The only data I can find for the BM-2R-A2 indicates that it is a mechanical limit switch, not a "temperature limit switch".

Obviously, you could use it as such with added hardware, and that may be the case. Is the switch rated for temperatures
in your application?
 
Although Honeywell does make a 22 Amp, HP rated swtch, I cannot verify that your switch is HP rated.
NOTE: There is no correlation between current rating and HP ratings of switches.
Is there a possibility that the electrical damage is precipitated by mechanical damage due to possible over travel of the operating mechanism?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 

Water or condensation getting to the switch?

______________________________________________________________________________
This is normally the space where people post something insightful.
 
I would think that if the switch appears to be rated for your application and is frying then your application is having a problem you might not realize. For instance the motor might be greatly overloaded causing a much much larger current than the switch can handle when the interruption occurs.

Keith Cress
kcress -
 
The referenced literature reads "... Designed with a hysteresis as small as 0,008 mm [0.0003 in]...". I claim no expertise, but wonder if contact chatter might be a factor. It might not take much vibration in the external mechanism to bounce the contacts.
 
temperature limit switch?

Are you trying to limit temperature or what? Sorry, I dont understand. I see only a micro switch

lukin1977
 
Some specs on the complete temperature limit switch may be helpful.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Thank you all for the inputs. It is a limit switch that is triggered by a temperature sensor/actuator. I will look into the possible contact chatter.

We also measured the load current. It runs at ~4.5A, with a ~11A inrush on startup.
 