Anyone know what the normal temperature rise of a fully loaded breaker terminal should be? I understand that the connection is (in most cases) rated to work safely up to 75 Degrees C.
I need to infrared scan hundreds of misc lighting and power panels mostly consisting of 20 amp branch circuits. Ideally I would remove all the panel covers to do this. But with limited resources that is no going to happen.
Instead I would like to use a threshold value of a breaker face being above adjacent breakers. Right now I am using 20 degrees C rise. If a breaker is 50 C and most of the other breakers in the same panel are 30 C I tag that panel for inspection. (Pull cover, check breaker terminal tightness, visually inspect wiring, and check loads.)
I need to know what temperature rise would be normal on a 20 amp breaker at a 16 amp load over the same breaker with no load. Also would the same temperature rise apply to larger breakers? They have more load, but also have larger connection areas.
I assume breaker designers have a temperature rise target for normal maximum load that is well below the safety limit of 75 degrees C.
Thanks,
Andy
I need to infrared scan hundreds of misc lighting and power panels mostly consisting of 20 amp branch circuits. Ideally I would remove all the panel covers to do this. But with limited resources that is no going to happen.
Instead I would like to use a threshold value of a breaker face being above adjacent breakers. Right now I am using 20 degrees C rise. If a breaker is 50 C and most of the other breakers in the same panel are 30 C I tag that panel for inspection. (Pull cover, check breaker terminal tightness, visually inspect wiring, and check loads.)
I need to know what temperature rise would be normal on a 20 amp breaker at a 16 amp load over the same breaker with no load. Also would the same temperature rise apply to larger breakers? They have more load, but also have larger connection areas.
I assume breaker designers have a temperature rise target for normal maximum load that is well below the safety limit of 75 degrees C.
Thanks,
Andy