Test of 90kV overhead lines 2

Status
Not open for further replies.

ses

Electrical
Sep 13, 2002
4
DK
Hi,
I am looking for typical electrical tests which must be performed before commissioning a 90kV overhead line.
Does any IEC standards or other equivalent standards describe such a test?
 
Replies continue below

Recommended for you

ses--

During my time with a big southern (US) electrical utility, it was my observation that they did NO testing of the electrical variety. The line construction crew foreman and others visually inspected the line before energizing.

The equipment at the ends of the line, circuit breakers, instrument transformers, lightning arrestors,protective realys, controls, etc., were all tested of course, but the line was only given a visual inspection.

oldfieldguy
 
Visual checks as oldguy said for radial lines. Make sure the safety grounds are removed. For loop feeds, check with phasing sticks before making the loop. Check phase to phase to test the tester before and after checking across the switch.
 