Hi,

our problem is this: we need a test plan to test the insulation of a 65 miles long power line (2-phase 11.5/23 kV). The line has been down for a couple of years and now we have to energize it again. There is possibly 2 disconnect switches along the line so it can be isolated in 3x20 miles long parts. Can a Doble M4000 be useful to do this test?

How would you proceed with this test?

Thanks

JLuc
 
Replies continue below

Recommended for you

I would get in my leetle peekup truck with a bag lunch and some binoculars and drive, baby, drive. Oh take a note book, a GPS, and digital camera to log any problems that will need to be followed up on.

Anything else will not cover leaning trees, cracked poles, bird nests, broken insulators, leaning poles, or rusted transformers.

Otherwise I guess you could just wait for someone's attorney to call.[infinity]

Keith Cress
Flamin Systems, Inc.-
 
I agree with the above. I don't know what any electrical test is going to tell you about the condition of the line unless there is a short.

After inspection, then try energizing one segment at a time, preferably by operating an electrically operated circuit breaker, rather than a manual switch.
 